Automatic Switch for generator and shore power
 

Automatic Switch for generator and shore power

Started by luvrbus, April 29, 2016, 08:12:32 AM

Previous topic - Next topic

luvrbus

What switch are most using the relay type or mechanical contact,surge protection or not ? I am leaning towards the Technology Research 40100 good or bad feed back  

thanks    
Life is short drink the good wine first

bevans6

I have automatic relay type, I guess.  switches live and neutral, has a priority input and a secondary input.  I put priority on the shore power.

Brian
1980 MCI MC-5C, 8V-71T from a M-110 self propelled howitzer
Allison MT-647
Tatamagouche, Nova Scotia

luvrbus

I was looking for a Todd but I guess they stop making those, they been around since the 60's and never gave any problems
Life is short drink the good wine first

eagle19952

Quote from: luvrbus on April 29, 2016, 08:34:43 AM
I was looking for a Todd but I guess the stop making those they, been around since the 60's and never gave any problems

there is a marine outfit that still deals in Todd designs... i am told.
Donald PH
1978 Model 05 Eagle w/Torsilastic Suspension,8V71 N, DD, Allison on 24.5's 12kw Kubota.

Geoff

The Todd is generator dominant.  So if you start your generator while hooked up to shore power do you fry the electrical system?  I made my own system that is shore power dominant.  I have screwed up and started my generator while hooked up to shore power and it won't let the generator into the 120v shore power system which would destroy everything.

--Geoff
Geoff
'82 RTS AZ

Boomer

Geoff brings up a good point.  I have an Iota and I never ever start the gen while on shore and vice versa.  Just in case.  Supposed to be protected but .........
'81 Eagle 15/45, NO MORE
'47 GM PD3751-438, NO MORE
'65 Crown Atomic, NO MORE
'48 Kenworth W-1 highway coach, NO MORE
'93 Vogue IV, NO MORE
1964 PD4106-2846
North Idaho USA

eagle19952

Quote from: Geoff on April 29, 2016, 05:26:50 PM
The Todd is generator dominant.  So if you start your generator while hooked up to shore power do you fry the electrical system?  I made my own system that is shore power dominant.  I have screwed up and started my generator while hooked up to shore power and it won't let the generator into the 120v shore power system which would destroy everything.

--Geoff


uhm...wouldn't it depend on how it's wired ?
Donald PH
1978 Model 05 Eagle w/Torsilastic Suspension,8V71 N, DD, Allison on 24.5's 12kw Kubota.

sixtyseven

From what I read, the Technology Research 40100 is also generator dominant (generator has priority).   That sounds backwards to me.  Why would you want to run your generator when you already have shore power?   Your generator is for when you don't have shore power available.  ???   Maybe I'm just backwards :)   I made my own automatic transfer switch, it has 50 amp priority, then 30 amp, then the gen., then inverter (inverter switches itself).  It seams to work good that way.   Ok...let the bashing begin.       
Mark,   I was brave enough (er....I mean foolish enough) to plug in both cords and fire up the gen at once, just to test it....worked good
Joe 
Oregon
1985  Prevost  8V92TA   HT740

Dave5Cs

If you have a good transfere switch mine takes care of it. I don't want an automatic genny start though. When if your generator starts and there is problems with the genny like overheating or leaky fuel line etc.
Dave5Cs
"Perfect Frequency"1979 MCI MC5Cs 6V-71,644MT Allison.
2001 Jeep Cherokee Sport 60th Anniversary edition.
1998 Jeep TJ ,(Gone)
Somewhere in the USA fulltiming.

sledhead

how dumb is this ..... I have a automatic transfer switch and the inverter also has one built into it ??? on the new coach

my old coach only has the inverter (Magnum Energy MSH4024RE Inverter/Charger ) which has a good built in transfer switch so with todays inverters why do you need a separate switch ?
dave   
dave , karen
1990 mci 102c  6v92 ta ht740  kit,living room slide .... sold
2000 featherlite vogue vantare 550 hp 3406e  cat
1875 lbs torque  home base huntsville ontario canada

blue_goose

Dave is correct, if you have 2 inverters both will work together and you always have 220volts without any effort on your part.  If you use the changover switch they are wired so you can't have gen and outside power at the same time.  Before the generator relay comes in the outside power relay drops out. 
Jack

luvrbus

Ok I have 2 Trace stacked sine inverters with a manual change over, here is the problem when the batteries are dead or removed like now I have no power when plugged in or even with the manual change over on the generator side and running.
I guess I could run the change over through the inverters they have the feature but all the gurus I talk to says this (the above) is not a uncommon hook up in fact some like it (I don't).
In all they all telling me to use a automatic change over wire it to make the shore power dominant bypassing the inverters and use the remote for inverters when needed right now the inverters are the dominant party  ;D and I don't want that    
Life is short drink the good wine first

TomC

I'm of the KISS theory. I have a separate circuit breaker box that is wired through the inverter that has its own automatic transfer switch. For shore/generator, I have a four 50amp circuit breaker box-two for shore power and two for generator with a sliding plate between the two that cannot allow shore or generator to be operated at the same time. Since my bus is wired straight 120vac, I only use one leg of the 50 amp shore power. I have both circuit breakers wired just in case one leg gives out but the other leg is still live. Good Luck, TomC
Tom & Donna Christman. 1985 Kenworth 40ft Super C with garage. '77 AMGeneral 10240B; 8V-71TATAIC V730.

luvrbus

 I am going to keep my auto start my EPS generator is well protected solo with it's Smart Start feature.I think Dick Wright,Tim Wice along with my backup if needed Tom Caffey have me headed in the right direction if I can just understand what they are telling me  ;D Tim draws me pictures which is good 
Life is short drink the good wine first

LuckyChow

Quote from: sledhead on April 30, 2016, 04:40:54 AM
how dumb is this ..... I have a automatic transfer switch and the inverter also has one built into it ??? on the new coach

my old coach only has the inverter (Magnum Energy MSH4024RE Inverter/Charger ) which has a good built in transfer switch so with todays inverters why do you need a separate switch ?
dave   

Because the transfer switch in the inverter passes through electricity that is coming in on the input side of the inverter, without regards to the origin.  If the electricity stops (or is not there) it transfers the inverters output to the "inverter made" electricity and disconnects the dead input.

The external transfer switch, which most folks wire in ahead of the inverter, will look at it's input lines (which are usually shore power/mains and generator) to see which one has electricity on it.  It will automatically switch to the source with electricity.  If both have electricity (if you were plugged in and had the generator running) they usually default to the generator.  The output side of this switch is usually wired to your breaker box.  Many installtions then have a sub panel off the main panel that they wire their inverter to.  Hope this made sense. 
Darryl
Smyrna GA
2000 Gillig Phantom