Generator Problems
 

Generator Problems

Started by Joebus, November 21, 2010, 04:40:58 PM

Previous topic - Next topic

Joebus

I have had problems with my genset (7.5 Onan DKD). sent it to a repair shop (Onan authorized) $ 1005.00 later and still not right.
Problem; no load= 119.8 VAC, as load is applied VAC decreases, 20 amps= 101 VAC, and down from there. I am sure they will take it in the shop again, but they are slow, (a month so far) and will continue to charge to replace parts until it is done.

I need to speed this up and maybe have some money left in the bank. This unit has a transformer regulator, I think it may be the problem, but the shop doesn't agree....yet. Any suggestions or prior experience

Do not want to leave for warmer area's without it. 
Joe Beleskey ,Stroud Ont. 50 Miles north of Toronto
1977 MC8, 8V71T, Auto

wrench

   Run it with a small load (20 amp),  does it smoke(black)?  check air filter, fuel filter,  rubber hose from the tank for crack,  It may bog down under load because starving for fuel or air.  With the same load, you can cut one injector at time by cracking the injector nut loose, that will tell you if the injector & each cylinder are working.  If one is bad there will not be much difference as the engine run when you open that injector.
     Are you in the south?
            wrench

Dreamscape

I sent you a PM that might help.

Paul
______________________________________________________

Our coach was originally owned by the Dixie Echoes.

desi arnaz

thomas f  Bethlehem n.h

Joebus

Thanks
wrench: motor never changes (1805 rpm) regardless of load...just VAC. We are still in Ontario getting cold
Paul: thanks for the PM, I have now posted as well.
Joe Beleskey ,Stroud Ont. 50 Miles north of Toronto
1977 MC8, 8V71T, Auto

robertglines1

guess you have checked the easy things..I had a 15 kw Onan that dropped voltage under load..cussed and pulled hair out--turned out to be worn out breaker on gen set..when the load came on  the breaker would heat up and not tripp but would loose partial contact--would have been better if it just tripped..no scientific reason..changed it and all was well..sometimes we can't explain the why--I don't have the education just the result. look for something that doesn't seem rite  discolored  loose connection  smell   corrosion..does voltage drop on both legs?
Bob@Judy  98 XLE prevost with 3 slides --Home done---last one! SW INdiana

Sean

If the RPMs are rock-steady (does not bog down under load, etc.) that tends to rule out governor problems as well as anything mechanically wrong with the engine.

If this is a transformer-regulated set, as you mentioned earlier, then there is a good possibility that all that is required is to "flash the field."  Your generator manufacturer should be able to provide instructions for this procedure on your set.

Alternatively, if this is an electronically regulated set, it sounds like a bad regulator.

If the set is transformer-regulated and the field is properly flashed, there is a simple terminal-strip adjustment, usually, to set the voltage.

If you post the complete model number from the nameplate I might be able to look some of this up.

-Sean
http://OurOdyssey.BlogSpot.com
Full-timing in a 1985 Neoplan Spaceliner since 2004.
Our blog: http://OurOdyssey.BlogSpot.com

Sean

Quote from: robertglines1 on November 22, 2010, 05:42:01 AM
... dropped voltage under load... turned out to be worn out breaker on gen set..

This is an excellent point -- I presume you are measuring the voltage AT THE HEAD, not at the load.  If not, you definitely want to measure at the head.  If there is a substantial difference between the voltage at the head and the voltage at the load, you could have a problem with the wiring such as too small a gauge, or loose connections at a terminal somewhere, or even a bad main breaker as Bob describes.

-Sean
http://OurOdyssey.BlogSpot.com
Full-timing in a 1985 Neoplan Spaceliner since 2004.
Our blog: http://OurOdyssey.BlogSpot.com

Joebus

Thanks to everyone for your responses. I took it back to the repair shop, they called a couple hrs later. Told me they could find anything wrong with it, and it muast be a bus problem. I returned and checked it at their shop and was ok so  I brought it home installed it as normal. Works great. So I am happy .
Thanks Joebus
Joe Beleskey ,Stroud Ont. 50 Miles north of Toronto
1977 MC8, 8V71T, Auto

FloridaCliff

Quote from: Joebus on November 23, 2010, 03:32:45 PM
Thanks to everyone for your responses. I took it back to the repair shop, they called a couple hrs later. Told me they could find anything wrong with it, and it must be a bus problem. I returned and checked it at their shop and was OK so  I brought it home installed it as normal. Works great. So I am happy .
Thanks Joebus

Joe,

That's generator repair speak for " we found what we didn't do or hook back up"

Glad your your back in the power generating business

Cliff
1975 GMC  P8M4905A-1160    North Central Florida

"There are basically two types of people. People who accomplish things, and people who claim to have accomplished things. The first group is less crowded."
Mark Twain

gus

Cliff is probably right, if he isn't it will happen again just when you most need it!!