Generator kinda fixed - Replace regulator next?
 

Generator kinda fixed - Replace regulator next?

Started by belfert, October 06, 2019, 10:44:39 AM

Previous topic - Next topic

belfert

Clifford recommended a new fuel filter as my generator might be starving for fuel.  I replaced both the fuel and the air filters and now the voltage is much better, but still not great.  I get about 127 volts at no load.  I had three rooftop A/C units and a 1,500 watt heater running and it dropped to around 113 volts initially.  After a bit I checked again and it was at 117 volts.  (I verified the compressors were all still running.)  I also checked at the generator and no difference.

A 10 volt drop seems high to me.  Should I still replace the regulator, or do I need to have the Cat 3011C engine checked at the Cat dealer?  It is better than it was.
Brian Elfert - 1995 Dina Viaggio 1000 Series 60/B500 - 75% done but usable - Minneapolis, MN

Geoff

Quote from: belfert on October 06, 2019, 10:44:39 AM
Clifford recommended a new fuel filter as my generator might be starving for fuel.  I replaced both the fuel and the air filters and now the voltage is much better, but still not great.  I get about 127 volts at no load.  I had three rooftop A/C units and a 1,500 watt heater running and it dropped to around 113 volts initially.  After a bit I checked again and it was at 117 volts.  (I verified the compressors were all still running.)  I also checked at the generator and no difference.

A 10 volt drop seems high to me.  Should I still replace the regulator, or do I need to have the Cat 3011C engine checked at the Cat dealer?  It is better than it was.

Your readings sound good to me!
Geoff
'82 RTS AZ

richard5933

Similar readings to what I have with my Perkins/Kohler 12.5kw
Richard
1974 GMC P8M4108a-125 Custom Coach "Land Cruiser" (Sold)
1964 GM PD4106-2412 (Former Bus)
1994 Airstream Excella 25-ft w/ 1999 Suburban 2500
Located in beautiful Wisconsin

DoubleEagle

Don't forget that the meter measuring the voltage might be off a bit, depending on its quality. Harbor Freight level, who knows; Fluke, probably dead-on accurate.
Walter
Dayton, Ohio
1975 Silvereagle Model 05, 8V71, 4 speed Spicer
1982 Eagle Model 10, 6V92, 5 speed Spicer
1984 Eagle Model 10, 6V92 w/Jacobs, Allison HT740
1994 Eagle Model 15-45, Series 60 w/Jacobs, HT746

belfert

The meter is about a $40 Greenlee meter purchased probably a dozen years ago.  Even if the actual numbers are a bit off I still don't like a 10 volt drop.

I had to replace the regulator previously because I was only getting about 56 volts.  That time the regulator was definitely at fault.  I set it to 127 volts at idle because it was dropping so bad.  If I had set it to 120 volts it would drop way too low.  I'll probably just send the new regulator back and live with what I have.
Brian Elfert - 1995 Dina Viaggio 1000 Series 60/B500 - 75% done but usable - Minneapolis, MN

oldmansax

You have 3 things in play here. The first would be the engine itself. Checking the frequency with a good meter will rule out engine problems. Standard A/C in the US is 60 Hz. On a generator, that is controlled by the RPM of the engine. Most gennies are either 1800 or 3600. A lot of people will set the no load frequency at 61 Hz. It should drop no more than 2 Hz under full load. That would put you at 59 Hz. under full load.

The next component is the generator (including the regulator).  A good quality generator will drop 2-7 volts under full load WHEN MEASURED AT THE GENERATOR.

The final component is the wiring. You can get a lot of voltage drop across the wiring, especially in a motor vehicle. If the first two checks read good, check the wiring for abraded or low capacity components.

TOM
1995 Wanderlodge WB40 current
1985 Wanderlodge PT36
1990 Holiday Rambler
1982 Wanderlodge PT40
1972 MCI MC7

belfert

I measured at the generator too and the difference between the generator and an interior outlet was less than one volt.

I don't think the meter I have can measure frequency good enough to try to check the frequency of the generator.  I don't know how to change the governor settings if frequency is off.

Thanks everyone for your help.  I have a number of things to check yet.
Brian Elfert - 1995 Dina Viaggio 1000 Series 60/B500 - 75% done but usable - Minneapolis, MN

buswarrior

Get a kil-o-watt from amazon.

Hz, amps, volts, killowatts used.

Every busnut should have one, or more of them.

Very useful measuring device.

https://www.amazon.com/P3-P4400-Electricity-Usage-Monitor/dp/B00009MDBU

Happy coaching!
Buswarrior
Frozen North, Greater Toronto Area
new project: 1995 MCI 102D3, Cat 3176b, Eaton Autoshift

belfert

I talked to Jeff at Powertech today and he thinks my 10 volt drop under a fairly heavy load is normal.  I have made arrangements to return the regulator I bought for $350.  The voltage issues turned out to be a combination of loose wiring and not changing the fuel and air filters in over 1,000 hours.  (Oil has been changed every 250 hours or once a year.)

I am still planning to check the frequency and a few other things.
Brian Elfert - 1995 Dina Viaggio 1000 Series 60/B500 - 75% done but usable - Minneapolis, MN

Oonrahnjay

Quote from: buswarrior on October 07, 2019, 05:47:31 AM
Get a kil-o-watt from amazon.

Hz, amps, volts, killowatts used.

Every busnut should have one, or more of them.

Very useful measuring device. ...

    Yep, I use mine just about every day.  When you have a total-carp Outback inverter, you have to.
Bruce H; Wallace (near Wilmington) NC
1976 Daimler (British) Double-Decker Bus; 34' long

(New Email -- brucebearnc@ (theGoogle gmail place) .com)

Dave5Cs

We got this one which is similar to the BW put up but it also has a menue, ad you can put in what you pay for your electric and see what each device is costing you. You set the rate, hours you want it to monitor etc. I find the onlyproblem with all these devices is that so far none of them take a 220 plug like for the dryer or AC units.

https://www.amazon.com/P3-International-P4460-Electricity-Monitor/dp/B000RGF29Q/ref=pd_sbs_60_1/142-0085577-1944600?_encoding=UTF8&pd_rd_i=B000RGF29Q&pd_rd_r=e6e2ef22-00f7-4311-bfdb-61c0d93298e7&pd_rd_w=JeJrS&pd_rd_wg=WGMkN&pf_rd_p=d66372fe-68a6-48a3-90ec-41d7f64212be&pf_rd_r=NM6QDJ9K1Q5CHQBVZT8P&psc=1&refRID=NM6QDJ9K1Q5CHQBVZT8P
"Perfect Frequency"1979 MCI MC5Cs 6V-71,644MT Allison.
2001 Jeep Cherokee Sport 60th Anniversary edition.
1998 Jeep TJ ,(Gone)
Somewhere in the USA fulltiming.

sledhead

I have 2 of these . one on each leg so I can keep track of how much power I am using . they work great

https://www.amazon.ca/gp/product/B014W3D1OC/ref=ppx_yo_dt_b_asin_title_o00_s00?ie=UTF8&psc=1

on amazon.com they are a lot cheaper


dave
dave , karen
1990 mci 102c  6v92 ta ht740  kit,living room slide .... sold
2000 featherlite vogue vantare 550 hp 3406e  cat
1875 lbs torque  home base huntsville ontario canada

DoubleEagle

Quote from: buswarrior on October 07, 2019, 05:47:31 AM
Get a kil-o-watt from amazon.

Hz, amps, volts, killowatts used.

Every busnut should have one, or more of them.

Very useful measuring device.

https://www.amazon.com/P3-P4400-Electricity-Usage-Monitor/dp/B00009MDBU

Happy coaching!
Buswarrior

The reviews are not always good; there are complaints of meltdowns and failures even when used below the rated capacity. It might be handy for light loads, only.
Walter
Dayton, Ohio
1975 Silvereagle Model 05, 8V71, 4 speed Spicer
1982 Eagle Model 10, 6V92, 5 speed Spicer
1984 Eagle Model 10, 6V92 w/Jacobs, Allison HT740
1994 Eagle Model 15-45, Series 60 w/Jacobs, HT746

belfert

Does a Kill-A-Watt help measure the big loads like the inverter battery charger or the rooftop A/C units?  The amp gauges others mentioned would seem like a better option.
Brian Elfert - 1995 Dina Viaggio 1000 Series 60/B500 - 75% done but usable - Minneapolis, MN

buswarrior

Kill-o-watt is for anything you plug in.

It is NOT for whole coach system measuring.

Inexpensive (around $20 online) way to measure how much power the things you want to put in the bus use, while they are still in the house.

Great for real world planning what your boondocking loads might be.

For instance, plug your house refrigerator into it for several days to get some real measurements of power used in your operation.

Sizing a battery bank and inverter is confidently approached when one really knows how much power devices use.

And it has a hz meter to check the generator.

Happy coaching!
Buswarrior
Frozen North, Greater Toronto Area
new project: 1995 MCI 102D3, Cat 3176b, Eaton Autoshift