Basement a/c question - Page 2
 

Basement a/c question

Started by richard5933, May 26, 2018, 04:27:05 PM

Previous topic - Next topic

eagle19952

Quote from: kyle4501 on May 27, 2018, 06:06:43 AM
107 seems low to me,
Low volts allows the unit to pull higher amperage which generates more heat.



that and factor high ambient temp in the bay and then age wear on the compressor and possibly a bad time delay (slug) the inrush start currents at 107v just isn't going to work for two units.
does one or the other function separately ?
good luck.
Donald PH
1978 Model 05 Eagle w/Torsilastic Suspension,8V71 N, DD, Allison on 24.5's 12kw Kubota.

oldmansax

Quote from: richard5933 on May 27, 2018, 10:24:35 AM
Are the voltage regulators adjustable? If not, anyone have a reliable source?

No. The Wanderlodge board has info on suppliers and maybe a few used ones.

TOM
1995 Wanderlodge WB40 current
1985 Wanderlodge PT36
1990 Holiday Rambler
1982 Wanderlodge PT40
1972 MCI MC7

thomasinnv

Quote from: oldmansax on May 28, 2018, 05:05:47 AM
No. The Wanderlodge board has info on suppliers and maybe a few used ones.

TOM
Thinking outside the box here, I wonder if anyone has found available or been able to retrofit an adjustable one? I know they are out there I had one on a generac years ago.

Sent from my SM-G930T using Tapatalk
Some are called, some are sent, some just got up and went.

1998 MCI 102-DL3
Series 60 12.7/Alison B500
95% converted (they're never really done, are they?)

TomC

Typically the voltage regulator will have an adjustment to boost it up a bit. HZ is controlled by engine rpm.  I adjust mine so I'm getting 60hz under load which will put the HZ around 63 or so under no load. Good Luck, TomC
Tom & Donna Christman. 1985 Kenworth 40ft Super C with garage. '77 AMGeneral 10240B; 8V-71TATAIC V730.

richard5933

Thanks for all the suggestions. Just got home and from a 4-day trip to Black River Falls. Quite a heat wave for us here in Wisconsin as temps approached 100 for a few days.

When we got home and plugged in the basement a/c units did work better, so I'm leaning towards the low-voltage being at least part of the problem. I'll get the meter out tomorrow when it's not so hot and check the performance of the generator (both hz and voltage). A new generator is not in the budget this year, so I'd like to keep this one as long as it does the job at hand. Hopefully I can tweak the settings a bit and make things work.

UPDATE: I just checked the generator output. It's spot on at 60hz and 117 volt at no load. One a/c takes it down to about 112 v and both bring it down to 108 v or so.

The rear a/c will run fine alone on the generator. It will also run fine when the front one is running at the same time. The front unit seems to cycle on and off more often than normal on generator, even more so if both are running at once. With both running on a hot day it cycles off more than on.

My thoughts are this...

Front a/c seems to be struggling more. I will open up the case and check the easy things (poor connections, binding fan, etc). I'll also connect my shore power monitor and see what current each unit draws individually to see if there's a difference.

Generator seems to be putting out the proper hz/volts at no load. Not sure what can be done to help it perform better under load. Suggestions are welcome. In the meantime I will start figuring out how to pay for a new one from Wrico. Not sure if I'll just throw a new head on or try to swing the whole new thing. Lots easier to just change the head, but then I'm stuck with the noise/vibration of the Perkins. Also have no idea when the Perkins will die or if it's being the problem. Since the generator only has two 30-amp breakers on the output legs, I'm thinking that the generator head is the problem.
Richard
1974 GMC P8M4108a-125 Custom Coach "Land Cruiser" (Sold)
1964 GM PD4106-2412 (Former Bus)
1994 Airstream Excella 25-ft w/ 1999 Suburban 2500
Located in beautiful Wisconsin

chessie4905

That's a good generator, Just needs some service and output adjustment. We had 2500 hours on our same unit in the 04. You do need to open the wiring area up and make sure you don't have any overheated connections due to loosening.
GMC h8h 649#028 (4905)
Pennsylvania-central

richard5933

Quote from: TomC on May 28, 2018, 12:23:30 PM
Typically the voltage regulator will have an adjustment to boost it up a bit. HZ is controlled by engine rpm.  I adjust mine so I'm getting 60hz under load which will put the HZ around 63 or so under no load. Good Luck, TomC
Best to set the hz to be at 60 with full load (both a/c units running plus battery charger) or comprimize by setting it with half load?

I don't see any adjustments on the regulator, but I can tweak the rpm setting to raise both hz and voltage a bit.
Richard
1974 GMC P8M4108a-125 Custom Coach "Land Cruiser" (Sold)
1964 GM PD4106-2412 (Former Bus)
1994 Airstream Excella 25-ft w/ 1999 Suburban 2500
Located in beautiful Wisconsin

brmax

Is this unit a electronic regulator circuit board. If so there may be a printed model number for some refference.


Good day

Floyd
1992 MC9
6V92
Allison

chessie4905

Please check your connections at generator, including the head. We found some almost burnt connections earlier in the hours and caught them before serious damage. That issue will cause voltage drop under load. The head should have a removable tin cover on end and box on top has small screws securing it. Yours is painted gold?
GMC h8h 649#028 (4905)
Pennsylvania-central

richard5933

From the comments and suggestions I've got the following checklist:

1. Inspect basement a/c unit for free air flow, fan movement, necessary lubrication, obvious mechanical issues, and/or any loose connections

2. Open inspection cover on generator head and check all connections for tight connections and/or other visible issues

3. Confirm tight connections inside generator control box

4. Confirm tight connections at manual transfer switch

5. Set generator engine RPM to produce 120v/60hz operation at load

6. Compare load from front and rear a/c units to be sure that one isn't pulling excessive current

FYI, generator is Kohler 12.5 RCOP67 with an output of only 10kw, not the 12.5 I early thought.

Am I missing anything?
Richard
1974 GMC P8M4108a-125 Custom Coach "Land Cruiser" (Sold)
1964 GM PD4106-2412 (Former Bus)
1994 Airstream Excella 25-ft w/ 1999 Suburban 2500
Located in beautiful Wisconsin

Jim Eh.

Check condenser and evaporator coils? Make sure no critters have set up their vacation condos. A blast of compressed air should flow through easily with no debris coming out.
"Some days it's just not worth chewing through the restraints"
Jim Eh.
1996 MC12
6V92TA / HT741D
Winnipeg, MB.

rdbishop

Richard,
Have you checked the thermo disk on the compressor. I had a split unit that did what yours is doing. I pulled the disk away from the comp. and let it run for a good while as I needed cold air. I also added enough 22 to let it sweat right  up to the comp.  Still running like that after 16 yrs

Richard                                                                                                                                                 

TomC

You should be able to keep that generator running for many more thousands of hours. I had a truck driver friend that his 8kw Powertech had 23,000hrs on is when he sold the truck-with one alternator head replacement from brush type to brushless. Good Luck, TomC
Tom & Donna Christman. 1985 Kenworth 40ft Super C with garage. '77 AMGeneral 10240B; 8V-71TATAIC V730.

luvrbus

You need a generator person if that Kohler has a 12.5 head  a HP setting will make it produce 12.5 K,the problem could the Perkins is at it's limit,it maybe the Perkins is due some TLC and not the head,those tough old generators with a little TLC    
Life is short drink the good wine first

chessie4905

I also think you need to have the generator serviced before issues down stream get costly. Have it done by an outfit that knows what they're doing and how to check and or change calibrations. Ask some questions of the establishment. There are good outfits out there, just have to search them out. Maybe an old outfit that is familiar with your unit and not going to try to make a sale on a replacement.
GMC h8h 649#028 (4905)
Pennsylvania-central