Need a rooftop a/c guru
 

Need a rooftop a/c guru

Started by Scott & Heather, July 06, 2016, 07:48:03 AM

Previous topic - Next topic

Scott & Heather

We purchased and Atwood air command rooftop air conditioner. It is one of the units that is controlled by a wall thermostat. Atwood has a digital wall thermostat, but we would like to use a house style thermostat. I would like this thermostat to Control both the furnace and the air-conditioner. I have not been able to get it to work even though I have connected the wires properly. When I called Atwood the gentleman I spoke to basically said it couldn't be done. He was very rude, and he did not want to hear any other options other than buying their Atwood thermostat. So I'm reaching out to the form for help. Is there a way that I can make a house thermostat work. Do I need to run 12 V to the air-conditioner?


Sent from my iPhone using Tapatalk
Scott & Heather
1984 MCI 9 6V92-turbo with 9 inch roof raise (SOLD)
1992 MCI 102C3 8v92-turbo with 8 inch roof raise CURRENT HOME
Click link for 900 photos of our 1st bus conversion:
https://goo.gl/photos/GVtNRniG2RBXPuXW9

thomasinnv

Scott there should be a control board inside the ac unit and yes you need to run 12v to it. If memory serves correctly, the thermostat wires from the furnace go to the control board, and the wall thermostat also connects to the control board. There are different versions of the control board and you need to have the right configuration to do what you are looking for.
Some are called, some are sent, some just got up and went.

1998 MCI 102-DL3
Series 60 12.7/Alison B500
95% converted (they're never really done, are they?)

TomC

Furnace control is just a simple on off affair. A/C control with thermostat needs 12v. Most household thermostats and A/C controls work with 24v ac, not the 12v dc that your unit works with. Just bite the bullet and use their thermostat. Good Luck, TomC
Tom & Donna Christman. 1985 Kenworth 40ft Super C with garage. '77 AMGeneral 10240B; 8V-71TATAIC V730.

brmax

plus 1 with what Tom mentioned
Brian without seeing a schematic for the model its going to be tough on us nuts.
no offense : )
In many units like your pic the 24v has been the trigger voltage for a long time opening the hi-voltage contacts through a coil or the likes, so one has to know the units need and its clarity you could say. To bump that nowadays some of the circuit boards are even using some new voltage "biased" stuff.
I am! curious as this has little to the operation, what I would think the board may have is a time delay on restarts. But without sensor wires from the unit showing these signal loads the board would just use the hokie method after a power out.

will keep an eye for any tips
good luck
Floyd
1992 MC9
6V92
Allison

Stormcloud

I installed a residential thermostat to control the gas furnace and the roof-mounted air conditioner in our 5th wheel trailer.
It has been a while since I did this, but I think this link should give you some insight.
Yes, it can be done.

http://rvroadtrip.us/library/digital_thermostat.php

Mark
Mark Morgan  
1972 MCI-7 'Papabus'
8v71N MT654 Automatic
Brandon, Manitoba, Canada in summer
somewhere near Yuma, Arizona in winter(but not 2020)

bigred

I just this went through this deal with putting new AC'S on my Prevost.Camping World used a 120x12v adapters on mine .Was only like 59.00 .I could not believe the crock of manure I had to go through for 3 AC'S.
Rhet Raby           137 Elk Mtn Rd       Asheville N c 28804             1993 Prevost XL

digesterman

It can be done, first one is a little tricky but the rest are easier. I put all wifi controlled in mine and love them, can turn them on and off, adjust and see temp anytime and anywhere I happen to be. Only way to go

Edited to add that I have 4 basement units. The Honeywells require 24v but you can buy 12 to 24v transformers
Lee
Le Mirage XL 45E
Detroit Series 60
470HP
111,230 original miles (11-2015)

Scott & Heather

Ok, so I am at a loss here. When the ac unit it energized, I get like 5 volts to two of the small wires (out of the four) in the thermostat wire harness. Seems to me that they've designed this to use their proprietary thermostat? Argh.


Sent from my iPhone using Tapatalk
Scott & Heather
1984 MCI 9 6V92-turbo with 9 inch roof raise (SOLD)
1992 MCI 102C3 8v92-turbo with 8 inch roof raise CURRENT HOME
Click link for 900 photos of our 1st bus conversion:
https://goo.gl/photos/GVtNRniG2RBXPuXW9

scanzel

Be care full if you burn up the control board in the air conditioner the thermostat won't be your only problem or expense plus you could void any warranty if the unit is new. My central thermostat for my Penguins requires 12v dc and two telephone 4 conductor cords to interconnect everything together.
Steve Canzellarini
Myrtle Beach, SC
1989 Prevost XL

thomasinnv

Yes scanzel is on to something. The older ac control boards can be used with a variety of thermostats as they are basically a series of relays (kind of but not really) and all they need is open or close contact to operate the various functions. The newer control boards utilise a network protocol of sorts to communicate with each other and you have to use a proprietary thermostat. If you are electrically savvy you could rewire with older style control boards and use older style thermostats, but for the cost and the trouble its really not worth it in my opinion.
Some are called, some are sent, some just got up and went.

1998 MCI 102-DL3
Series 60 12.7/Alison B500
95% converted (they're never really done, are they?)

luvrbus

I don't have any idea how the they do it but the upper end conversions like a Marathon Prevost or Newell they control all 5 units through the Crestron system,that would be a little expensive,I do like the idea that the fan motor has a 1 minute delay and stops after the compressor stops when the temp setting has been reached   
Life is short drink the good wine first

brmax

Your on to something now Scott
As we were talking about a little earlier some of the hi volt contacts still use the base of systems with low volts like 24 to the coils.
With the pc stuff from the 80's the boards typically use a 5volt reference to signal. So there may well be a basic board system in the unit now, I don't have a clue to help but wished I did, sorry
have a good day with the task
Floyd
1992 MC9
6V92
Allison

Geoff

Years ago this subject came up and it was revealed that WalMart sold an inexpensive wall thermostat that would work in an RV.  I use Colman wall thermostats that have both heating and cooling adjustments. 

--Geoff
Geoff
'82 RTS AZ

Seangie

Quote from: Scott Bennett on July 06, 2016, 08:55:06 PM
Ok, so I am at a loss here. When the ac unit it energized, I get like 5 volts to two of the small wires (out of the four) in the thermostat wire harness. Seems to me that they've designed this to use their proprietary thermostat? Argh.


Sent from my iPhone using Tapatalk
Scott,

Where are you getting your +12, +24v from?

It should be coming from the coach.

A couple things here (Nick tell me if Im off base here)

1.  Make sure your thermostat can work with a DC voltage.  As Tom said earlier it might need a low voltage AC signal instead of a DC signal. 

2. Once you figure out what voltage the thermostat can work with then feed the thermostat with that voltage.  So if it works with 12v DC then grab a positive and negative 12v wire from your batts and power up the thermostat.  If its not 12v dc then provide whatever voltage the thermostat needs.

3.  With just the positive and negative hooked up to the thermostat (it may also ask for a ground as well to work properly.  Just run a wire to your bus frame)  click the thermostat on in such a way that the Air conditioning would power up.  Check the voltage of the lead wire thats supposed to go to the Air Conditioner.  Check that voltage.  That voltage needs to match what the control board on the AC unit requires to power on.  For example - My coleman Mach 8 control board (and for the mach 8 its a seperate board that doesnt come with the unit.  You have to buy the control board and plug it into the roof unit to work with a thermostat) uses a 12v signal.  In my case if the thermostat does not put out a 12v signal then the roof air wont turn on.

4.  If the thermostat does not put out the correct voltage then you will need the correct piece of electronics to change that signal from the voltage that the thermostat puts out to the voltage the roof air needs. Ie 24v DC to 12v DC.

Id upload a diagram but Im in Canada until next week and network is spotty plus Im on vacation.  And there is a cold beer in the fridge waiting for me.... 

Haha.  Just call me at 5am tomorrow and Ill talk you through it. 

-Sean

Sent from my SM-N920P using Tapatalk
'Cause you know we,
we live in a van (Eagle 10 Suburban)
Driving through the night
To that old promised land'

Scott & Heather

Lol thanks Sean! Sorry for waking you up the other day. Atwood kindly is sending me their proprietary thermostat free of charge asap. Like it shipped today from Indiana. Very nice of them. Surprised me actually. Once I get it and get the ac operating, I'll experiment more with it. Right now I just don't have the time. We did get power today finally :)



Sent from my iPhone using Tapatalk
Scott & Heather
1984 MCI 9 6V92-turbo with 9 inch roof raise (SOLD)
1992 MCI 102C3 8v92-turbo with 8 inch roof raise CURRENT HOME
Click link for 900 photos of our 1st bus conversion:
https://goo.gl/photos/GVtNRniG2RBXPuXW9