Circuit Breakers vs. Fuses. (House System)
 

Circuit Breakers vs. Fuses. (House System)

Started by Chaz, August 08, 2011, 05:45:58 PM

Previous topic - Next topic

Chaz

Hey guys,
I'm sporting a Xantrex 4024 with eight 6 volt batteries for my house system. I was going to buy a 400 amp breaker but they are a bit on the pricey side. I have been using an ANL fuse block up till now. I have also been using 250 amp fuses. I'm thinking I might  be a little "over protected" and thinking I may step up to a 400 amp fuse as I "think" that is what I should be using. The reason being: I will blow a fuse if I have both AC's running and the shore cord loses juice. I would have thought the batteries should have just taken over but they don't get a chance. ?? ?? ??
Thoughts...............
Thanx,
Chaz
Pix of my bus here: http://s58.photobucket.com/albums/g279/Skulptor/Motor%20Coach/
What I create here:   www.amstudio.us

"Imagination is more important than knowledge". Albert Einstein

bevans6

This is on the DC side, right?  Fuses are probably the better way to go, relatively easy to change and not all that expensive.  4,000 watts at 24 volts (maybe you might draw your batteries down lower than that and develop higher current) is only 166 amps.  Add 50% for the surge, that's your 250 amps.  There are two schools of thought here - protect the equipment by fusing at the max draw you want it to ever see, or protect the wiring - fuse to protect the ampacity of the cable and hardware you are using.  400  seems a lot, check out what your wiring can support.

Brian
1980 MCI MC-5C, 8V-71T from a M-110 self propelled howitzer
Allison MT-647
Tatamagouche, Nova Scotia

belfert

We went through this discussion just recently here.  Sean was pretty adamant that you want a T class fuse instead of a breaker.  The reasoning seemed to be that a T class fuse would react faster than a breaker.  Solarseller.com should have what you want if you can't find a T class fuse locally.  (Website is a bit disorganized, but the prices are pretty decent.)

I use a 225 amp DC breaker I got for free, but I guess I really should have a T class fuse.
Brian Elfert - 1995 Dina Viaggio 1000 Series 60/B500 - 75% done but usable - Minneapolis, MN

Sean

The correct fuse or breaker depends on cable size.  If you use 0000 cables, Xantrex specifies a 250-amp breaker or a 400-amp fuse.  Xantrex recommends Class-T fuses, as do I.  Breakers are another issue altogether, and I can't give you a specific recommendation here without further research; suffice it to say, most are not fast-acting enough for this application.

DC protection sizing can be found on page 23 of your manual.

-Sean
http://OurOdyssey.BlogSpot.com
Full-timing in a 1985 Neoplan Spaceliner since 2004.
Our blog: http://OurOdyssey.BlogSpot.com