My Bus is wired for 50 amp, I had it plugged in with a 50 – 30 dogbone with a 30-15 adapter (got that see pictures).
Well I washed the bus, and standing barefoot in the water touching the stainless or lugnuts I got a shock?

So I re plugged with the 50-30 dogbone to a 30-amp outlet and no more shock.
Well I had to keep trying right, 50-30-30 wishbone with 2, 30-15 adapters no shock.

Ok the 50-30-30 wishbone with 2, 30amp lines for 60amp (more power right?).
Wrong tripped both 30 amp breakers, shut down my inverter display panel.

I know what happened but I thought I would throw this out there for your morning read and to see the different answers.
MCI-9
Sussex county, Delaware.
See my picture's at= http://groups.yahoo.com/group/busshellconverters/
That's Not Oil Dripping under my Bus, It's Sweat from all that Horsepower.
----- This space for rent. -----

Ednj

MCI-9
Sussex county, Delaware.
See my picture's at= http://groups.yahoo.com/group/busshellconverters/
That's Not Oil Dripping under my Bus, It's Sweat from all that Horsepower.
----- This space for rent. -----

Ncbob

Ed, other than to advise you to NEVER wash a vehicle which is plugged into AC in your bare feet...but then you already discovered that it's not a good idea.

My view, and it may be disputed by others with more and better credentials than I, is that a voltage (whether AC or DC) is always seeking to complete the circuit so it is seeking ground. In the case of DC that ground would be a negative source. In the case of AC, of which we're talking here, it is less selective as to that source of ground or neutral. Now there is a difference.

Neutral is the completion of the circuit as far as the load is concerned. But AC is Alternating Current...and it has a direction of flow. We think of Positive, Load and Neutral in an AC circuit and sometimes forget that half of the time the 'positive is neutral' and vice versa. But as to the direction of flow we wire the circuit from source to the breaker, to the load and to Neutral so both the wiring and the load are protected.

Neutral is common with earth ground only insofar as it goes back to the powerhouse to seek that earth ground.
That could be many miles and voltage takes the path of least resistance which in this case might have been you.
To reasonably insure ourselves a measure of safety we add an Earth Ground (or equipment ground) to a circuit to shorten that path of resistance to ground.

My guess in your instance was that you (your bare feet) standing in water (one of the best conductors known) were if fact that path of least resistance and you got bit. Too, there might be a problem with the earth ground (the 4th pin in the plug) making a complete enough contact.  And here's where the conjecture comes in.

It is doubtful that you can duplicate exactly the conditions prevalent at the moment of your contact (or that you'd care to) to trace exactly what caused you to get shocked. All you can do is to take whatever steps are necessary to insure that your wiring is to Code...even then there are no guarantees if you run around barefoot in puddles!

You have my empathy for your experience but as my Dad used to say, "Use it as a learning experience and be smarter for it."

Hope this helps.

Bob

Len Silva

The simple answer is that if you got a shock, you had a less than ideal ground.  However, that also means that there is an electrical "leak" to the coach body somewhere which shouldn't be there.  Perhaps a neutral to ground connection that should not be there.  Perhaps the inverter bonding relay is not working as it should or the transfer switch is not working right.  It would seem that your 15 amp adapters were no providing a good ground.

If everything were perfect, you would not get a shock even without any ground.  It is there to protect against a fault.

The two 30 amp breakers tripping must mean that you were effectively connected to 220 and the two legs were tied together somewhere downstream.

Len

Hand Made Gifts

Ignorance is only bliss to the ignorant.

HighTechRedneck

Quote from: Ednj on June 11, 2008, 04:24:15 AM
My Bus is wired for 50 amp, I had it plugged in with a 50 – 30 dogbone with a 30-15 adapter (got that see pictures).
Well I washed the bus, and standing barefoot in the water touching the stainless or lugnuts I got a shock?

So I re plugged with the 50-30 dogbone to a 30-amp outlet and no more shock.


15 amp outlet had ground and neutral reversed?

Quote from: Ednj on June 11, 2008, 04:24:15 AM
Ok the 50-30-30 wishbone with 2, 30amp lines for 60amp (more power right?).
Wrong tripped both 30 amp breakers, shut down my inverter display panel.


30 amp outlets were on opposite phases?

TomC

I believe in simplicity.  While I have a 50 amp shore plug, I only use one side of it since the bus is wired for straight 120vac.  While this limits my shore power to 6,000 watts, I can still run two A/C's with power left over to use the water heaters.  I really like the fact that I'm not constantly worried about balancing the loads out when the generator is running.   Just something to consider-I will wire my next conversion the same.  Good Luck, TomC
Tom & Donna Christman. 1985 Kenworth 40ft Super C with garage. '77 AMGeneral 10240B; 8V-71TATAIC V730.

bobofthenorth

I'll take a shot at it - one of your 30 amp outlets has the hot and neutral reversed, as does the 15 amp outlet you were using while washing.  Or you had a 15 amp extension cord with the hot and neutral crossed while washing.

R.J.(Bob) Evans
Used to be 1981 Prevost 8-92, 10 spd
Currently busless (and not looking)

The last thing I would ever want to do is hurt you.
Its the last thing but its still on the list.

Ednj

Can't stump any of you.
MCI-9
Sussex county, Delaware.
See my picture's at= http://groups.yahoo.com/group/busshellconverters/
That's Not Oil Dripping under my Bus, It's Sweat from all that Horsepower.
----- This space for rent. -----

Nick Badame Refrig/ACC

Guy's,

Remember, with an uneven load on both legs of 50A, the nutral carries the current......

Never wash your bus with it pluged it!

Nick-
Whatever it takes!-GITIT DONE! 
Commercial Refrigeration- Ice machines- Heating & Air/ Atlantic Custom Coach Inc.
Master Mason- Cannon Lodge #104
https://www.facebook.com/atlanticcustomcoach
www.atlanticcustomcoach.com

Nick Badame Refrig/ACC

Ed,

Here are some more amps if you need more power.. ;D

Nick-
Whatever it takes!-GITIT DONE! 
Commercial Refrigeration- Ice machines- Heating & Air/ Atlantic Custom Coach Inc.
Master Mason- Cannon Lodge #104
https://www.facebook.com/atlanticcustomcoach
www.atlanticcustomcoach.com

Ednj

Quote from: Nick Badame Refrig. Co. on June 11, 2008, 08:39:32 AM
Ed,

Here are some more amps if you need more power.. ;D

Nick-

Cool Nick, now Daniel wants to come over with his guitar.

While we're at it,
I have my house battery bank and the start battery bank tied together with an auto solenoid.
Works great.
The inverter charges the start batteries when plugged in & the alternator charges the house bank when driving.
When I drive the bus with the generator running the dash amp meter jumps (like flashers)'
Is it because the generator is putting out more than the alternator?
???
MCI-9
Sussex county, Delaware.
See my picture's at= http://groups.yahoo.com/group/busshellconverters/
That's Not Oil Dripping under my Bus, It's Sweat from all that Horsepower.
----- This space for rent. -----

Tenor

ROCK AND ROLL!!!!!!!!
Glenn Williams
Lansing, MI
www.tenorclock@gmail.com
2001 MCI D4500
Series 60 Detroit Diesel
4 speed Spicer

ktmossman

Damn...  Nick must look like a one-man band trying to play all those guitars and stomp all those tiny pedals.  ;D

I have 1K watts in my little GK bass system we can throw in...
Kevin Mossman
2006 MCI J4500
Dallas, TX

Bob Gil

Quote from: Ednj on June 11, 2008, 09:47:15 AM
The inverter charges the start batteries when plugged in & the alternator charges the house bank when driving.
When I drive the bus with the generator running the dash amp meter jumps (like flashers)’
Is it because the generator is putting out more than the alternator?
???

Could it have some thing to do with them both trying to charge the same abtteries and the regulators not ikeing what the other one is doing?
Fort Worth, Texas where GOD is so close you don't even need a phone!

1968 GM Bus of unknown model 6V53 engine (aftermarket) converted with house hold items.

Had small engine fire and had no 12 volt system at time of purchase. 
Coach is all 110 w 14KW diesel genrator

TomC

Some cool looking old amps!! TomC
Tom & Donna Christman. 1985 Kenworth 40ft Super C with garage. '77 AMGeneral 10240B; 8V-71TATAIC V730.