As Tom said, you'll need (a lot) more batteries to power a 3kW inverter!   3kW at a nominal 12V is a whopping 250A  -  that's almost at starter motor current levels!   The generally-accepted wisdom on the Northern Arizona Wind & Sun solar forum is that drawing more than about 100A from 12V batteries will run you into Mr.Peukert and his limitations on battery currents, unless you have a battery bank a lot larger than your two Group 31s.

To put this into perspective, I have 2kW of solar panels that will charge eight golfcart and/or L16 batteries through two Morningstar TS-MPPT-60 charge controllers.   Even with a minimum of 900Ah from eight GC-2s (or more if I use L16s), I don't plan on having a TSW inverter larger than 1500W for general AC loads.   I will also use 4/0 cables from each bank of four batteries to their isolator and from the two isolators to the main DC load center  -  for a 3kW inverter running off 12V I would suggest paired 4/0 cables to minimize voltage loss.

Back to the original question.   Assuming your inverter is about 90% efficient, you could be dissipating up to 300W of heat from it at full load!   That needs some serious thought about airflow and heatsink orientation.   For that much potential heat production I would mount the inverter on perforated 1/4" aluminum sheet  -  definitely no wood anywhere near it!

John
1990 Crown 2R-40N-552 (the Super II):  6V92TAC / DDEC II / Jake,  HT740.     Hecho en Chino.
2kW of tiltable solar.
Behind the Orange Curtain, SoCal.

Beesme

If I were to use 3 k yes I agree. I just got a good price on it . The only power that will be going through it is a refrig that most of the time is only at a couple hundred watts even start up is only around 1 k and that is at start up. I don't know very many peeps using  3 k unless you were using ac I guess . This is for keeping beer and food cold . Nothing but fridg and 2 lights tied in.
Bruce E.                                                                        62 pd4106 vs730.                   
Gonic N.H.

pvcces

Idle current is significant in any low cost new inverter. You might be able to get the specs from the maker.

Good luck.

Tom Caffrey
Tom Caffrey PD4106-2576
Suncatcher
Ketchikan, Alaska

Beesme

I am designing a cradle so inverter can suspend from ceiling upright . But just for info I have been monitoring temps of mounts and staying at 87deg. But for safety reasons I will move . Thanx for all the input.
Bruce E.                                                                        62 pd4106 vs730.                   
Gonic N.H.

Beesme

Sorry eagle 19952 . Yes inverter is something like that .
Bruce E.                                                                        62 pd4106 vs730.                   
Gonic N.H.

mung

So you don't want your inverter to be inverted?   :P
Vern in Central Florida
PD-4104-772

Beesme

Lol mung no I guess not inverted haha omg made me chuckle!
Bruce E.                                                                        62 pd4106 vs730.                   
Gonic N.H.