Fuses on Circuit breakers....

Started by wildbob24, May 24, 2013, 08:04:46 AM

Previous topic - Next topic

wildbob24

This one is for the electrical gurus in the room.

My Buffalo has 6 circuits up front that have glass fuses connected between the wire and the circuit breaker. All of these circuits are for the various lamps and lights on the bus. The glass fuses are all 30amp and the circuit breakers vary with one being 5amp, 2 are 8amp and 3 are 10amp. See attached image.

I'm hoping someone more knowledgeable than I can explain the logic of this set-up because I'm not seeing it.

Thanks,

Bob

P8M4905A-1308, 8V71 w/V730
Custom Coach Conversion
PD4106-2546, 8V71, 4sp
Greenville, GA

bevans6

I tried hard to come up with a legitimate reason for having high amp fuses in the load path with a low amp breaker.  All I could come up with is the obvious - minor overload, resettable breaker so you can change a lamp or whatever, major overload the fuse blows and you can find the short.  The problem with that is the breaker will blow before the fuse every time.  So the fuse becomes a last ditch protection for the major overload and the breaker failing.  \maybe the fuse is fast blow while the breakers are slow blow.   Maybe that is the answer but it's all I can come up with.

Brian
1980 MCI MC-5C, 8V-71T from a M-110 self propelled howitzer
Allison MT-647
Tatamagouche, Nova Scotia

TedCalvert

Breakers have a quality known as interrupting capacity. Fuses do too. If the available fault current exceeds the interrupting capacity of the breaker the contacts may weld together. Guess what happens then?

Uglydog56

The problem with those resettable breakers is they keep resetting even though your fault hasn't necessarily cleared.  Eventually the breaker fails and you have a fire. The fuse prevents that. Manually resettable breakers would be a simpler solution, bit it works as is.

Sent from my SCH-I535 using Tapatalk 2
Rick A. Cone
Silverdale, WA
66 Crowny Crown "The Ark"

gus

These auto resetting type breakers were once used on older light aircraft and later banned and replaced by fuses for the above posted reasons.

However, that doesn't explain the huge different differences in ratings on your bus.
PD4107-152
PD4104-1274
Ash Flat, AR