anyone have a diagram on properly hooking up the solar panel to a chinese EPRC-ST,12v or 24v autowork controller /charger..the panel is putting out 17.7 volts to the charger ,,to the battery terminal its putting 15.4 volts ..when you hook it up to the batteries,,3-12v deep cycle marine batteries ..it puts out 12.0 volts ..both green lights are "on" the charger indicating that its working ,,,the batteries are not charging ..Any suggestions??  thanks ..I 'm a newby at this,,Pete

Jerry32

All I can tell you is the minus from the panels should not be connected to anything but through the controller. Depending on what the controller is supposed to be is should be giving more than `12 volts to the batteries.  Jerry
1988 MCI 102A3 8V92TA 740

Len Silva

It could be that nothing is wrong except the batteries are low and it's trying to charge them.

What is the battery voltage without the charger hooked up?
Can you put an ammeter in the circuit to see what is happening.  The panels are rated at about 5 amps.  That's not much if the batteries are very low.  It could take a very long time at that rate.

Try connecting only one battery for a few days and see what happens.  It should get up to 13.5 or better but it might take a while.

Hand Made Gifts

Ignorance is only bliss to the ignorant.

JohnEd

Everything Len said,

Connect the charger to a fully charged bat and check for "fully charged FLOAT" voltage and I think that is 13.5.

John
"An uneducated vote is a treasonous act more damaging than any treachery of the battlefield.
The price of apathy towards public affairs is to be ruled by evil men." Plato
"We can easily forgive a child who is afraid of the dark; the real tragedy of life is when men are afraid of the light."
—Pla

pete36330

thanks for all the advice ..I'll start in the morning,,checking...