Quote from: Dlsnow on February 13, 2015, 07:26:44 PM
Make sure to size your inverter main breaker. I had to move mine to a 150amp (dc rated) from an 80 to accommodate the startup load.

Dave
I'll be buying a Cotek SK2000 which is rated at 2,000W continuous and 4,000W surge, so it'll have a 200A ANL fuse and 4/0 cable from the batteries.   I hope to be drawing less than 100A from the batteries for A/C running loads.   All my switches/cables/busbars/isolators/pass-throughs/etc are rated for 250A minimum.