Title: Grounding to bus chassis
Post by: Scott & Heather on July 22, 2016, 04:25:35 PM
My electrician is doing an amazing job of installing our electrical system on our coach. He's using all 12 and 14 gauge THHN wire and he's an artist in how he runs the wire...using liquid tite everywhere and rubber grommets throughout. He has done a ton of research on how to properly wire the 120 V system of an RV. He's come to the conclusion that we need to ground to the chassis. He did do this. He's also going to figure out a way to bond the generator power. Just wanted to get everyone's opinion here how they did this. We are looking at making a special plug that just plugs into the generators outlets to do this...


Sent from my iPhone using Tapatalk
Title: Re: Grounding to bus chassis
Post by: Jim Eh. on July 22, 2016, 09:18:18 PM
Hey Scott,
Hope all goes well and quick with the electrical. Since TV is soooo pitiful here if you get some time, could you fix the link to your progress picture site? Gilligan is really getting old!
Title: Re: Grounding to bus chassis
Post by: niles500 on July 22, 2016, 09:19:01 PM
Plenty of info in the archives on neutral ground bonding and transfer switches, worth the read, remember 4 wire and only one neutral ground bond AT the source - hth
Title: Re: Grounding to bus chassis
Post by: bevans6 on July 23, 2016, 03:36:28 AM
You tie the electrical system ground to the chassis permanently and to the ground of any power source, be that inverter, generator or outside power.  For outside power, that is done through the power cord.  You bond neutral to ground only once at a time, at the source of the power.  Normally that means that neutral is switched on and off the same as the live lines are, as you connect to each power source.  Doing that with a plug is fine, as long as you remember to disconnect the plug if the generator is off.  I use a automatic transfer switch and leave the plug connected to the generator all the time.

Brian
Title: Re: Grounding to bus chassis
Post by: gumpy on July 23, 2016, 06:34:00 AM
You said "outlets".  You probably only use one outlet, but it may be possible to use one for each leg of your 120v panel.

Yes, it's ok to make up a plug (actually receptacle) for this. You can incorporate the neutral/ground bond in the receptacle from the generator. You would also then have a similar receptacle for the shore power, and one for the inverter (also incorporating neutral/ground bond). There would be a single plug pigtail from the electrical panel that you move between the three receptacles to select your power source. This is the most simple and fool proof method of power source selection, though it does require complete disconnect of power in the bus when switching and would require you to shut off your high loads when switching, but you should do that anyway, even if you use a ATS.

The battery bank negative, A/C distribution panel, inverter and generator grounds should be bonded to the coach body at a single point. Just weld a bolt to the frame and bond them all there.  In reality, the generator will be bonded to it's frame so will be bonded to the coach where it's bolted down. Typically the same for the inverter and A/C panel.

Title: Re: Grounding to bus chassis
Post by: oltrunt on July 23, 2016, 12:39:37 PM
There does seem to be a range of answers  on this topic.  Just to further muddy the waters, here is what OSHA says about grounding/bonding generators in RV's:
https://www.osha.gov/OshDoc/data_Hurricane_Facts/grounding_port_generator.pdf (https://www.osha.gov/OshDoc/data_Hurricane_Facts/grounding_port_generator.pdf)

If you aren't acquainted with Mike Sokol's "No Shock Zone, it is a very easy to understand explanation of all things electrical in RV's--in particular,how to prevent getting shocked.  While Mike's info can be purchased on line, it also can be viewed on several sites.  I just came up with this one:
http://rvtravel.dreamhosters.com/category/rv-living/rv-safety/no-shock-zone/. (http://rvtravel.dreamhosters.com/category/rv-living/rv-safety/no-shock-zone/.)

Perhaps the single most important lesson from the article(s) is that there be only one neutral/ground bond for each electrical supply source(and why).  Hope this helps, Jack
Title: Re: Grounding to bus chassis
Post by: HB of CJ on July 23, 2016, 12:48:21 PM
A 12VDC, (24VDC) chassis dedicated grounding bar running the length parallel to the main chassis boxed rail.  This bar has multiple grounding points.  All the grounding needs of the DC CHASSIS electrical system runs through this bar.

As far as the HOUSE high voltage alternating current grounding needs, perhaps somebody can tell us how it works and how it should be done.  I suppose one does not want to mix up the two, (2) separate electrical grounding systems?
Title: Re: Grounding to bus chassis
Post by: oltrunt on July 23, 2016, 07:27:29 PM
HB, exactly.  Read both the above articles and the wax paper over the crystal ball will be removed!  Jack
Title: Re: Grounding to bus chassis
Post by: bevans6 on July 24, 2016, 04:45:36 AM
Quote from: HB of CJ on July 23, 2016, 12:48:21 PM
A 12VDC, (24VDC) chassis dedicated grounding bar running the length parallel to the main chassis boxed rail.  This bar has multiple grounding points.  All the grounding needs of the DC CHASSIS electrical system runs through this bar.

As far as the HOUSE high voltage alternating current grounding needs, perhaps somebody can tell us how it works and how it should be done.  I suppose one does not want to mix up the two, (2) separate electrical grounding systems?

You can keep the AC ground separate from the DC grounds for wiring purposes, you need to always keep low voltage Dc and higher voltage AC wiring separate, but the actually chassis ground connects are tied together.  You should always connect the ground of both AC and DC wiring to the chassis of the bus.  according to the OSHA article, you also should drive a ground stake if running off the generator and powering up a trailer, so that ain't going to happen.  Unless someone has a source for 60 mph ground stakes...  :)
Title: Re: Grounding to bus chassis
Post by: oltrunt on July 24, 2016, 07:08:34 AM
The OSHA article actually says, "frame of a portable generator need not be
grounded (connected to earth) and that the
frame may serve as the ground (in place of
the earth)"----and,  (the) "frame of a portable generator need not be
grounded (connected to earth) and that the
frame may serve as the ground (in place of
the earth)."  Therefore no 60 mph ground rods needed :D.   
Jack
Title: Re: Grounding to bus chassis
Post by: bevans6 on July 24, 2016, 10:44:44 AM
The OSHA article says that (above) if the generator  supplies only equipment
mounted on the generator and/or cord and
plug-connected equipment through
receptacles mounted on the generator.

this is what would apply to a generator supplying power to a bus:

If the portable generator is providing electric
power to a structure by connection via a
transfer switch to a structure (home, office,
shop, trailer, or similar) it must be connected
to a grounding electrode system, such as a
driven ground rod. The transfer switch must
be approved for the use and installed in
accordance with the manufacturer's installation
instructions by a qualified electrician.
Title: Re: Grounding to bus chassis
Post by: Dave5Cs on July 24, 2016, 11:20:35 AM
And we're off, My cat wants to watch too!... :o
Title: Re: Grounding to bus chassis
Post by: luvrbus on July 24, 2016, 11:26:15 AM
We always had to drive a ground rod on a portable generator to comply with OSHA standards in Oklahoma maybe that has changed now with those idiots 
Title: Re: Grounding to bus chassis
Post by: gumpy on July 24, 2016, 12:34:10 PM
I didn't read it. I don't really care what OSHA says.
Title: Re: Grounding to bus chassis
Post by: oltrunt on July 24, 2016, 01:37:21 PM
Bevans6, I get what you are saying and I agree if the genny is sitting outside the bus on the ground.  On the other hand if the genny is a permanent install in the bus then bonding to the genny frame is the ticket.  Jack
Title: Re: Grounding to bus chassis
Post by: eagle19952 on July 24, 2016, 01:52:08 PM
Quote from: oltrunt on July 24, 2016, 01:37:21 PM
Bevans6, I get what you are saying and I agree if the genny is sitting outside the bus on the ground.  On the other hand if the genny is a permanent install in the bus then bonding to the genny frame is the ticket.  Jack



airplanes have the same problem.
Title: Re: Grounding to bus chassis
Post by: Scott & Heather on July 24, 2016, 07:58:20 PM
He did actually refer to Mikes site and followed his instructions to a T. So I guess we are solid.


Sent from my iPhone using Tapatalk
Title: Re: Grounding to bus chassis
Post by: Oonrahnjay on July 26, 2016, 08:59:21 AM
Quote from: gumpy on July 24, 2016, 12:34:10 PMI didn't read it. I don't really care what OSHA says.   

    Mike Sokol (the "No-Shock" guy) says that ground rods are unreliable.  Despite going to the best ground source there is, there's a fair amount of resistance/impedance in the rod, ground-to-rod interface, wiring, connections, etc.  If there's an electrical defect and the resistance/impedance is lower between an energized coach and the ground through the body of a person touching it, the ground rod does nothing and the person carries all the juice -- with possibly fatal results.  That's pretty simple - a rod may help you but don't depend on it to save your life.

    I'm not an electrical expert but that sounds logical to me.
Title: Re: Grounding to bus chassis
Post by: bevans6 on July 26, 2016, 09:28:57 AM
OSHA is kind of like the bible.  It sets out somewhat reasonable common sense rules that cover a lot of situations, and if you follow them you will probably be OK.  It doesn't cover everything, and sometimes you do something else.

Brian