Title: Inveter Charging ?
Post by: luvrbus on July 02, 2016, 06:41:23 AM
I have stacked inverters both have charging ( SW4024) ? do I need both inverters charging or will 1 be enough
Title: Re: Inveter Charging ?
Post by: Oonrahnjay on July 02, 2016, 07:38:30 AM
Quote from: luvrbus on July 02, 2016, 06:41:23 AMI have stacked inverters both have charging ( SW4024) ? do I need both inverters charging or will 1 be enough   

     How large is your battery bank now?  What's the charge rating on the SW4024?   (You've got *TWO* SW4024's???  Whuttcha planning to do, light up Times Square?)
Title: Re: Inveter Charging ?
Post by: bevans6 on July 02, 2016, 08:08:52 AM
I would just use one.  They sense the current flow vs voltage to tell how charged the battery is and using two stands a good chance of confusing that.  They have a really high charge rating, unless your battery bank is a couple of thousand AH one should be able to keep up.
Title: Re: Inveter Charging ?
Post by: eagle19952 on July 02, 2016, 08:45:39 AM
try it. you can always turn the charge portion of one off..
Title: Re: Inveter Charging ?
Post by: niles500 on July 02, 2016, 08:55:14 AM
My Magnums both charge although one usually does the bulk of the charging, never read the manual to find out why FWIW
Title: Re: Inveter Charging ?
Post by: luvrbus on July 02, 2016, 10:37:48 AM
The inverters are adjustable from 0-120 amps they are both set on 60 amps ea.Bruce the system is set up for 6-8D AGM as of right now I just bought some cheap 6 -12v deep cycle batteries till I get the system figured out and the way I want it lol if you want to call 800 bucks for 6 batteries cheap
Title: Re: Inveter Charging ?
Post by: Oonrahnjay on July 02, 2016, 01:53:21 PM
Quote from: luvrbus on July 02, 2016, 10:37:48 AMThe inverters are adjustable from 0-120 amps they are both set on 60 amps ea.Bruce the system is set up for 6-8D AGM as of right now I just bought some cheap 6 -12v deep cycle batteries till I get the system figured out and the way I want it lol if you want to call 800 bucks for 6 batteries cheap   

     A few people have suggested just trying it but do you have problems getting a full charge in the time you have available?  The idea of having two electronic devices that could crosstalk or feed back to each other kind of scares me.  I'd contact Trace (or whoever owns/makes those inverters) and get the approval of their tech support.  At just a guess you might need to charge 300 Amp/hr (assuming your 6 batts are 100 amps each) and you have a 50% state of charge), you'd get a full charge out of one 60-amp charger in 5 hours (yeah I know it doesn't work like the calculations in real life, but that should be a good guide).  Is it often that that's not enough?

     I'd hate to see anybody cook a set of batteries - even "temporary" ones.  Good luck.
Title: Re: Inveter Charging ?
Post by: gumpy on July 02, 2016, 01:58:30 PM
Read the manual, it talks about this issue when stacking.

I'm pretty sure you only use one for charging.

The charge rate is based on your battery size and 60 amps is way too high.  There's a formula in the manual. Basically 1/5 the bank capacity.

Title: Re: Inveter Charging ?
Post by: Seangie on July 02, 2016, 02:07:53 PM
Cliff -

Id do just one system charging.  Leave the other one on your Generator battery or start batts if you dont have them tied to the house batts.

Also - if one ever fails you'll have a backup.

You can adjust the charging amperage based on wiring not based on battery bank or load.  Dont go putting 120amp charging on anything less than 2 aught wire.  Id set it at 100amps for charging.

-Sean.
Title: Re: Inveter Charging ?
Post by: gumpy on July 02, 2016, 02:47:16 PM
Cliff, be very careful with the advice you're getting in this thread. The SW series inverter bulk charge amps setting is set using AC amps, and should be set based on the capacity of your battery bank, not based on cable size or phases of the moon or anything else. Read page 66 of the owner's manual, rev B, Sept 1, 1999.

Title: Re: Inveter Charging ?
Post by: eagle19952 on July 02, 2016, 05:10:50 PM
here's what page 66 says...
The battery charger
settings will automatically adjust if the temperature compensation sensor is installed.
If it is not installed,
the settings should be adjusted manually to allow for the typical battery temperature. This may require
seasonal readjustment for optimum performance.


so. hook up the temp comp sensor... mine have been on a sensor for ever. i have only ever set the battery type and AC in breaker setting. and that was over the phone with xantrex.

Title: Re: Inveter Charging ?
Post by: Jon on July 02, 2016, 06:59:27 PM
It is common practice on professional conversions to have both inverters charging house batteries at the same time.

What is important is to first identify how the coach is being used. If it is used for dry camping a lot then both are going to restore the batteries to full charge quickly. The flip side to that is if the coach runs from power pole to power pole or the generator is run when not connected to shore power the batteries will likely always be fully charged so instead of a high charge setting, the inverters can be set to a relatively low value. The reason for that is if connected to 50 amp shore power and a lot of electrical loads are being used, like the ACs then a high charging current is going to trip the shore power breaker.

It is all about energy management and doing what makes sense given the various circumstances.

But whether you charge with one inverter or two is unimportant. What is important is how the charging current level is set given the circumstances. I am a power pole to power pole RVer so mine are both charging, but are set to 10 amps for charging. If I dry camped a lot I would set them at about 65 amps for charging to keep generator run time to a minumum.
Title: Re: Inveter Charging ?
Post by: Dave5Cs on July 02, 2016, 07:21:24 PM
Clifford also I found out on mine If I am at home and plugged into a 15 amp circuit I have to adjust the incoming amps to the my inverter to say  14amps or it will start feeding off the house batteries to make up the difference when the charger comes on if I forget and have it on higher from being plugged into a 50 amp pole.
Dave
Title: Re:
Post by: thomasinnv on July 05, 2016, 06:15:26 PM
The bts only adjusts charging voltage, not amperage. Regardless if a bts is installed you still need to set the proper charge rates. Most stacked inverter setups will use only one inverter to charge the bank if one unit is capable of putting out the required capacity based on the bank size. If not, then both units will charge at half the required capacity. Some units are capable of running in master/slave configuration(the master unit controls all functions of both units)
Title: Re: Inveter Charging ?
Post by: B_K on July 05, 2016, 09:14:51 PM
Where is Sean Welsh when ya need him?
He knows all about this stuff!
;D  BK  ;D
Title: Re: Inveter Charging ?
Post by: luvrbus on July 05, 2016, 09:26:43 PM
Quote from: B_K on July 05, 2016, 09:14:51 PM
Where is Sean Welsh when ya need him?
He knows all about this stuff!
;D  BK  ;D

Living the good life,I am going to call him with another question I have in the next week
Title: Re:
Post by: thomasinnv on July 06, 2016, 08:07:31 AM
Cliff for the quick and easy solution just calculate your required charge rate for the bank you have and set one inverter to that figure, disable the charger on the other one. This will work just fine.
Title: Re: Inveter Charging ?
Post by: luvrbus on July 06, 2016, 08:30:01 AM
The Trace guru in CO Springs Co walked me through it,I now have one doing the bulk charge and the other does the float it's doing great.
I plan on just using 1 inverter and removing the other all plugs and fixtures stay hot when I turn either off.I still do not like the generator and shore power needing to run through the inverters first but that is another project for a different day 
Title: Re:
Post by: thomasinnv on July 06, 2016, 08:37:18 AM
Are you saying all power goes thru the inverter first? Not the main panel? I wouldn't like that either. My generator/shore goes to the main panel, then a 30 amp breaker feeds the inverter from there, then from inverter to a sub panel for inverter fed circuits.
Title: Re: Inveter Charging ?
Post by: RJ on July 06, 2016, 11:33:20 AM
Clifford -

I sent you a private message.

RJ
Title: Re: Inveter Charging ?
Post by: brmax on July 06, 2016, 11:52:53 AM
Seems I have heard the inverter as the lead before, and with some follow-up looking around long time ago. I found a few post here and elsewhere with Seans transfer box build he did early on. Sure was a cool build.
I believe in that setup he used the transfer as the lead from pole and genny sure worth taking another look at!

Floyd
Title: Re: Inveter Charging ?
Post by: bevans6 on July 06, 2016, 12:40:28 PM
I wired mine so that the power from pole or generator goes to a standalone ATS, from there it goes to the non-inverter panel and to the inverter both, through the inverter to the inverter panel.  So I have two breaker panels, one that can be fed from the pole or the generator, and one that can be fed from the pole, generator and the inverter (in that order of priority).