This weekend i went to or state Park. Parked her and got out to hook her up. I noticed that the 15 and 30 amp Breakers had GFCI's and I thought OH KNOW! You guys taught me that my bus does not like GFI's and I can't use them. Of course they tripped the breaker on the 30 and 15 amp plugs. I don't have a 50 am so i was dead in the water. It was 93 degrees and it was very humid around 80%. I hated to do it but I had to break the news to my little boys that we would have to go home. Very sad time in bus land. My question is: What can I do to get around this. Can it be fixed? Would i have to upgrade to a 50 amp? All the state parks in IL have switched to this system and if I want to go I have to Change. Please give me any advice you might have.
Yes, you can probably fix it. The only problem I know of is some inverter/chargers have a neutral-ground connection and/or a capacitor in the circuit that fools the GFI.
With an ohmmeter, check for continuity between neutral and ground on the 30 amp plug. There should be no connection between the two. If there is continuity (and there is if you are tripping GFI's), isolate circuits one at a time by flipping breakers, disconnecting appliances or what ever you have to do until you find it.
You should see no connection between neutral and ground or between hot and ground.
well, you need to figure out why your bus is tripping the GFI breaker. I would start by checking my grounds, make sure neutral is separate from ground on the bus itself, and disconnect things until I can plug in the bus and NOT trip the breaker. Then, start connecting things back up. You can install a temporary (or permanent) GFI outlet where you plug your bus in at home. If it trips that, and it should to start, you can use it to test with.
Brian
Mike,
The right answer here is that you need to figure out why you are tripping GFIs, because that might be indicative of a larger problem.
The most usual reason why this happens is a common wiring error: connecting ground and neutral together in the main panel. In an RV, ground and neutral must be kept separate.
The second most common reason is use of a transfer switch that does not switch neutral. This causes the neutral to ground bond in the generator to carry back to the rest of the coach wiring.
Either of these problems is a serious safety hazard and should be fixed. That should cure the GFI tripping problem.
The third most likely problem is that there is an appliance on board that has an internal ground fault, and this, too, should be corrected.
There is a potentially non-hazardous source of these nuisance trips, which is at the inverter, which will have a ground-to-neutral bonding relay, so that the inverter operates safely when it is powering loads. Some inverters, notably the Xantrex SW series, will trip GFI's due to filter capacitance. If either of these is your problem, there are some workarounds we can discuss.
Bottom line: find the culprit first, then we can address the way to resolve it.
-Sean
http://OurOdyssey.BlogSpot.com (http://ourodyssey.blogspot.com)
Wow, you guys type a lot faster than I do.
Quote from: Len Silva on June 13, 2010, 08:45:42 AM
... isolate circuits one at a time by flipping breakers, disconnecting appliances or what ever you have to do until you find it.
Just a word of caution: turning off a circuit breaker will generally not isolate a ground fault. That's because the breaker is in the hot side of the circuit, and does not disconnect the neutral side. So if there is a ground to neutral fault in an appliance, neutral current from the neutral bus in the panel will actually flow out to the appliance on the appliance's neutral, then back to the panel ground on the appliance's ground, even if the breaker for that appliance is off.
This is also going to be true for inverters and anything else hardwired as well, so I am afraid that while Len's advice is correct, you're really going to have to physically disconnect each circuit.
I would start by looking in the three most obvious places: the main panel itself, the transfer switch, and the inverter.
-Sean
http://OurOdyssey.BlogSpot.com (http://ourodyssey.blogspot.com)
when i plugged it in and it tripped the first time, i went back to the bus and turned off the main breaker. Thus taking power away from the whole system. It still tripped after this. I took the plug apart and could not find any thing wrong with it. Came home and plugged it in to the house power on a plug that is not gfi protected ( only breaker ) she works fine.
Does code require GFI on 30 amp RV service these days? I suppose they are being extra cautious, but I expect they are going to get a number of complaints.
Everything outside (and in the bathroom) around here is supposed to be protected by a GFI.
With what is known about them, I'd wonder if the install of a GFI at the post would be a good due diligence defense on the campground's part for an unintended electrocution?
Exposes all the RV's that have the neutral/ground co-mingled?
Now, from the other side of the fence, does the presence of a properly functioning GFI give the camper some piece of mind about the potential for shoddy campground wiring?
happy coaching!
buswarrior
If the pedestal had a 50 amp plug you should have used a 50 to 30 amp adapter.
You should carry adapters of all configurations to over come problems like this.
Alan
Quote from: Madmike on June 13, 2010, 09:19:04 AM
when i plugged it in and it tripped the first time, i went back to the bus and turned off the main breaker. Thus taking power away from the whole system. It still tripped after this. ...
Again, ground faults are not interrupted by circuit breakers. You need to physically disconnect circuits, including the neutral wires, until you isolate the problem.
Quote from: belfert on June 13, 2010, 09:51:04 AM
Does code require GFI on 30 amp RV service these days? I suppose they are being extra cautious, but I expect they are going to get a number of complaints.
Not required by the NEC, but required by some state codes which are more stringent. Also a good idea from a safety perspective anyway.
We've encountered this in a few parks, and it was a great annoyance until we figured out how to keep our SW4024 from tripping them (disconnect the filter capacitor).
Quote from: Alan Baker on June 13, 2010, 10:33:28 AM
If the pedestal had a 50 amp plug you should have used a 50 to 30 amp adapter.
Sorry, but this is dangerous advice. You need to figure out why you have a problem and fix it -- you could be putting yourself at risk.
Secondly, 50p-30r adapters are dangerous in general. That's because your cord is only rated for 30 amps, but the pedestal breaker will pass 50 amps. If you are going to carry and use one of these for those very rare occasions when you will find a 14-50R but no TT-30R, make absolutely certain that you have a working 30-amp main breaker in the circuit aboard the coach.
-Sean
http://OurOdyssey.BlogSpot.com (http://ourodyssey.blogspot.com)
Sean is 100% correct. Find & fix the problem; the life you save my be one of your son's!!!
I can plug into any 110 GFIC and not trip it. I also have several GFIC's within my coach.
Like Sean said, #1- look first to see if the ground wires and the white neutral wires are on separate bus bars. They can not share the same one like a house. I had to add a separate insulated bus bar at my sub panel circuit breaker box to accomplish this.
Question for Sean;
I have a 30 amp main as my shore line enters the coach. The hot and neutral are switched through the 30 amp. circuit breaker. The ground is not switched.
The ground is always grounded to shore when plugged in, the coach chassis is grounded to this, the 110V generator is grounded to this, all 110V wiring from my sub panel main breaker are grounded to this.
I have a 30 amp transfer switch that switches the blk & wh. only, it's default is shore power and activates with a time delay when the generator is turn on.
The 5KW generator has it's own 40 amp. circuit breaker box. In the gen. brk. box I have the hot with a circuit breaker, I have the neutral and ground tryed to the same barrier strip. I have a ground strap at the generator to chassis The ground then goes through the auto transfer box ( just passes through ) and to a separate insulated ground barrier strip in the sub box for the circuit breakers, this grd. then goes to the 30 amp main CB box to it's own separate lug. If the generator is running with the shore cord plugged it is also ground to shore.
I do not have a inverter. I have always thought this was 100% correct. Am I wrong anywhere in my thinking? I am not trying to high jack this thread I thought this question is basically what is being discussed.
Thanks for any input.
Craig,
So long as the generator/shore transfer switch also transfers the neutral wire, you should be OK. Even if both shore and generator are energized, the transfer switch should ensure that the coach's main neutral is connected to only one or the other, but not both. So the ground-to-neutral bond will still only be in a single location.
-Sean
http://OurOdyssey.Blogspot.com (http://ourodyssey.blogspot.com)
We've encountered this in a few parks, and it was a great annoyance until we figured out how to keep our SW4024 from tripping them (disconnect the filter capacitor).
Sean, how does affect the inverter?
That is one of the cautions in the Trace manual that it will trip GFI breaker.
I do the workaround with 30/50 adapter and set the Trace incoming at <30 amps.
Even is you incorporate the neutral ground bonding relays per Trace all you end with is a relay race in which the GFI trips before the relays can respond with correct bonding setup.
Bill
Madmike,
You have not indicated what your equipment list is on your bus. What inverter are you using? Is there a generator? Transfer switch? etc...
Sean's advise should be heeded. It's possible it's caused by your inverter, but it's also possible you have another problem elsewhere. We really need more info to
help diagnose your problem. Start with the equipment list.
Did you wire your coach or was it wired by someone else?
craig
This may not apply here but some coaches (bluebirds in particular) have polarity fault indicator lights that will trip a GFI. This is discussed at length on the Wanderlodge board. I think there is a work around but I didn't read the entire thread. I can look it up if anyone is interested.
TOM
Quote from: Bill B /bus on June 13, 2010, 06:52:15 PM
... how to keep our SW4024 from tripping them (disconnect the filter capacitor).
Sean, how does affect the inverter?
It won't affect the inverter at all.
What might be affected is anything sensitive to RF interference, such as AM radios. The capacitor in question is intended to reduce RF noise generated by the inverter that affects other sensitive devices.
Quote
...
Even is you incorporate the neutral ground bonding relays per Trace all you end with is a relay race in which the GFI trips before the relays can respond with correct bonding setup.
This is a separate problem, and there are several workarounds. For a long time, we'd slip a dollar bill between the contacts of the bonding relay while we hooked up the power. As soon as the power was connected, the relay opened, the dollar bill fell out, and we were good to go.
Eventually I got tired of opening the ATS enclosure (where our bonding relay lives) every time, and I made myself a special "adapter."
Here is where I have to say, like the Mythbusters, "Don't try this at home: I am a trained professional." Specifically, the adapter in question is definitely not "to code." It is, however, "temporary" and intended only to fix this specific problem.
What I did was to make a 4" long adapter with a standard 20-amp receptacle on one end (NEMA 5-20R) and a mostly standard 15-amp plug on the other end (NEMA 5-15P). I took my Dremel and cut 3/8" off the ground tang of the plug. This makes the ground tang, which is normally just a tad longer than the hot and neutral tangs, now a tad shorter than those tangs.
When I need to hook up to a GFCI, I first put this adapter on the end of my 20-amp shore cord (yes, I carry a separate, 10-gauge, three-wire, 50' cord for connecting to distant 15-, 20-, and 30-amp receptacles), connect the cord to the coach, and then plug in to the GFCI receptacle. Since the hot and neutral now make contact first, the bonding relay lifts before the ground makes contact, and, voila, no GFCI trip. Once the plug is fully inserted, the ground is once again safely connected. The very short margin between the two lengths means that if I don't insert the plug far enough for the ground to make contact, then it will fall out altogether when I let go.
I only carry a "15-20 amp" version of this adapter, but it is made with 10-gauge (30-amp) wire. I have found little need for a dedicated 30-amp (NEMA TT-30) version, but one could be made. In the extremely rare case where I want to connect to a 30-amp GFCI, I simply use my TT-30P to 5-20R adapter at the pedestal, and the magic adapter at the end of the 10-gauge shore cord, and make the connection between the magic adapter and the 30/20 reducer last. If I am at all worried about the intervening 20-amp rated plug and receptacle, I will dial the SW4024 input power down to 20 amps (normally on a 30-amp shore service we dial it down to 24 amps).
This is not for the faint of heart and there is a certain amount of risk if you do it incorrectly. But realistically there is no other way to connect a properly wired SW-series inverter with the required external bond relay to a GFCI-protected shore service, short of using an isolation transformer.
-Sean
http://OurOdyssey.BlogSpot.com (http://ourodyssey.blogspot.com)
I will have to check as to what type of invertor I am using. As far as I can tell there is not transfer switch but I am new to this. I just plug it in and the 120volt stuff works, when the generator is running the 120v stuff works also. I don't switch anything. I pluged it in at my house using my 15amp adapter and it works fine as long as i am not on a GFI protected plug. This bus was done by a professional bus conversion shop and there has never been any problems with the electrical, it is the GFI's that it does not like. I will get it inspected either way. When I get home tonight I will look it over and see if I can give you guys some part numbers.
This is a problem I've had on a couple of occasions with my Trace inverter. Why would a company such as Trace build a piece of equipment knowing it won't work when used in conjunction with a GFI? Why should you have to "jerry-rig" something to "fool" it?
Are all inverters like this or is it just Trace?
Gary,
The SW series inverters were never designed for RV use. The RV listing (and software) was added as an afterthought. This is why there is no internal bonding relay, and why no thought was given to cord-and-plug usage.
You take the bad with the good. What makes these units so great is the load-support feature, which is a direct result of the grid-tie legacy. No other RV inverter has this feature.
In later models, Trace made the ground wire for the filter capacitor a quick-disconnect affair for exactly this reason. The bonding-relay related problems are external to the inverter, so Trace can hardly be blamed for that one (other than blaming them for not integrating the feature in the first place).
There really is no way around this without electronic control and sequencing of the ground bond.
-Sean